User: jmargolis79, Location: minneapolis
Asked on: Monday, January 10, 2011 at 9:18 pm EST
Answered on: Tuesday, May 14, 2024 at 12:04 am EDT
Question: Can you have the motor disconnect inside of a large box (24"x24" hoffman nema 3r). Box doesn't have any windows. The box is insight and within 50' of motors.The box has 4 disconnects for 4 motors all in the same area. I think it has 2 problems.1. If you are working on 1 of the fans and have to tag out that 1 in the box you are exposed to the other 3 disco's 480 voltage.2. If tthe box id closed you couldn't see your lock out, and it would be a hazard to have the box open if any of th motors were running.
NEC Code Requirements
NEC 430.102(B)(2): Motor disconnecting means must be located within sight from the motor location and within 50 feet of the motor, unless a sight-within requirement is specified elsewhere in the NEC. NEC 312.5(C)(5): Enclosures housing disconnecting means shall not be used as junction boxes or to enclose other equipment, except controllers.
Interpretation
Based on the provided information, it appears that placing the motor disconnects inside the Hoffman Nema 3R box may violate the following NEC requirements:
1. Visibility of Disconnects
The box does not have any windows, which means the disconnects would not be visible from the motor location, violating NEC 430.102(B)(2).
2. Enclosure Usage
The box is being used to enclose disconnects for multiple motors, which would violate NEC 312.5(C)(5), as it is not specifically designed for controllers.
Hazards
As you mentioned, working on one motor while the other three are live could expose workers to hazardous voltages. Opening the box while the motors are running would create a hazard due to the presence of exposed energized equipment.
Recommended Solution
To address these concerns, it is recommended to relocate the motor disconnects to a dedicated enclosure that meets the following requirements:
Visibility
The enclosure should be visible from the motor location and within 50 feet of the motors.
Enclosure Type
The enclosure should be suitable for the location (e.g., NEMA 3R for outdoor use).*
Enclosure Usage: The enclosure should be used solely for housing the motor disconnects. Flag for review