Question: Trying to plan a project where I will take a Hoffman enclosure that will house two motor starters that control 1 50hp motor, and 1 20 horsepower motor that goto a mixer. The feeder will come from a 600a 480V MDP. Without getting to deep into distances, what is the best way to start figuring my cb size? I would like to also have a cb in the hoffman enlosure with a rotary handle on the outside. So do I size enclosure CB the way the code says for multiple motor loads? Should I oversize my MDP CB? Just trying to figure out the best coordination.
Enclosure Circuit Breaker Size Determine the full-load current (FLA) of each motor. Multiply the FLA by the Code-specified multiplier for multiple motors: 1.25 for two motors. Add the resulting currents to calculate the total load current. Select a circuit breaker with a trip rating equal to or greater than the total load current.
MDP Circuit Breaker Size Determine the short-circuit current (SCC) at the location of the MDP. Select a circuit breaker with an interrupting rating greater than or equal to the SCC. Oversizing the MDP circuit breaker is not recommended as it reduces coordination and selectivity.
Enclosure Coordination Select an enclosure circuit breaker that has a lower trip rating than the MDP circuit breaker. This ensures that the enclosure circuit breaker will trip before the MDP circuit breaker, isolating the fault to the enclosure.
Rotary Handle Circuit Breaker Use a circuit breaker with an external rotary handle to provide easy access for resetting the breaker. The handle should be located outside the enclosure to prevent accidental operation.
Overall Coordination The overall coordination scheme should ensure that the enclosure circuit breaker trips before the MDP circuit breaker, providing selective protection. The MDP circuit breaker should be sized to protect the feeder and downstream devices, but not be oversized to avoid reducing coordination.
Example
50 hp motor
FLA = 70 A
20 hp motor
FLA = 30 A
Total load current
(70 A + 30 A) x 1.25 = 125 A
Enclosure circuit breaker
150 A
MDP circuit breaker
Assuming an SCC of 30 kA, an interrupting rating of 42 kA or higher is required*
Coordination: Enclosure circuit breaker (150 A) trips before MDP circuit breaker (42 kA) Flag for review