Topic: Isolated ground wire run indepently

User: anbm, Location: Illinois

Asked on: Tuesday, January 11, 2011 at 10:41 am EST
Answered on: Tuesday, May 14, 2024 at 12:06 am EDT

Question: We have an radiology equipment which requires both ground + isolated ground wires. The electrical panel (H1) that feeds this radiolody equipment doesn't have an isolated ground bar.From radiology equipment will we run ground + isolated ground wires in same conduit back to panel 'HA', the regular ground wire will be bonded to equipment ground bar in panel 'HA'. From panel 'HA', the isolated ground wire shall continue to run in a separate conduit and be terminated to nearest building groounding system (i.e building steel, water metal pipe) without going back to main building service source switchboard. Will this acceptable?Because if we run this isolated ground wire all the way back to main service switchboard, we have to shut down all panels upstream of 'HA' until the isolated ground wire reachs the main service switchboard and this can create problem, cost issue. Thanks!

Yes, your proposed solution is acceptable according to the NEC (National Electrical Code) and industry best practices.

Grounding Arrangement

The equipment grounding conductor (regular ground wire) should be bonded to the equipment grounding bar in panel HA. The isolated ground conductor should run in a separate conduit and be terminated to the nearest building grounding system (e.g., building steel, water metal pipe).

Reasons for Separate Conduit for Isolated Ground



Safety

Running the isolated ground wire in a separate conduit ensures that it does not come into contact with other electrical circuits, reducing the risk of interference or ground loops.


NEC Compliance

The NEC requires isolated ground conductors to be run in a separate conduit to prevent them from becoming part of the equipment grounding system.

Termination to Nearest Grounding System

Terminating the isolated ground wire to the nearest building grounding system is acceptable because it provides a low-resistance path to ground for any fault currents. Running this wire all the way back to the main service switchboard is not necessary and could be impractical as it would require shutting down upstream panels.

Additional Considerations:
The isolated ground conductor should be properly labeled and identified at termination points for easy identification and maintenance. The building grounding system should be adequate to handle any potential fault currents from the radiology equipment.* Ensure that the isolated ground conductor is sized appropriately according to NEC requirements.By following these guidelines, you can safely and effectively install the isolated ground wire for your radiology equipment. Flag for review