Question: This is concerning a project in California that went through plan check and approval in 2006. I am looking for the specific code that requires installation of plenum rated devices (fire life safety) to be installed. I know the NFPA 262 and NFPA 90A address plenum and cabling and I understand that NFPA 255 concerns testing of such devices but I need to find the part in the code where it requires installation of these approved devices in a plenum space.Thank you for your time/Vr
California Building Code (CBC)Section 717.1 (2013)"Plenum spaces shall be protected with fire-rated floor-ceiling and wall assemblies, as required by Section 714.1."Section 714.1 (2013)"Fire-rated wall assemblies and fire-rated floor-ceiling assemblies shall meet the requirements of Chapter 7, Referenced Standards Code."Referenced Standards Code (RSC)Section 305.3.11 (2013)"Plenums shall be provided with fire-rated floor-ceiling and wall assemblies having a fire resistance rating of not less than 2 hours."NFPA 90A-2015Section 6.3.3 (g)"Installed in plenum spaces, equipment shall be listed as suitable for use in such spaces."Section C.6.3.3 (g)"The requirement for equipment to be listed as suitable for use in plenum spaces does not imply that the equipment must be listed for use in corrosive environments, hazardous (classified) locations, or other specific conditions where special suitability may be necessary." Flag for review