User: ejohnson, Location: Lockport, IL

Asked on: Tuesday, January 11, 2011 at 3:58 pm EST
Answered on: Tuesday, May 14, 2024 at 12:07 am EDT

Question: NEC Article 310.60(C)(2)(b) states that ??an ampacity derating factor of 6 percent per 300-mm (1-ft) increase in depth for all values of rho shall be permitted.?. Does the derating factor not decrease with an increase in depth to a point at which it becomes zero? If not, using this derating method, there is a point at which the conductor will have negative ampacity.Example: 15kV 1/0 AWG shielded single conductor copper cable, no neutral (select smallest neutral size in table)Using table in IEEE Std. 835-1994 (pp. 349):75% load factor, 90 Rho, 90?C max. conductor temp. from table, 105?C desired conductor temp. rating, 25?C ambient temp. used in table, 21?C desired ambient temp., 0 for temp. rise due to dielectric loss, 0 for new temp. rise due to dielectric loss, 234.5 inferred temp. of zero electrical resistance, 48? burial depth to top of duct bankUsing formula from IEEE Std. 835-1994, Section 3.4.1 (pp. Intro-10): Adjusting for ambient temperature, the multiplier obtained is 1.03.Using formula from IEEE Std. 835-1994, Section 3.4.2 (pp. Intro-10): Adjusting for maximum conductor temperature, the multiplier obtained is 1.08.Derating for depth: 1.00 ? 1.5(.06) = .91Ampacity rating for 1/0 cable with 1/6 neutral: 139AI = 139*1.03*1.08*.91 = 140A (rounding down)Same example with 240? (20-ft) burial depth to top of duct bank:Derating for depth: 1-(20*12-30)/12*.06 = -.05I = 139*1.03*1.08*-.05 = -7A (rounding down)How can this be possible? Also, is there no reason to account for the difference in ampacity between conductors at the top of a duct bank and conductors at the bottom of the same duct bank?

Derating Factor

The derating factor does decrease with an increase in depth, but it does not reach zero. The formula for the derating factor is:

0.6(D - 0.3)
where: D = depth in meters (or feet) 0.3 = depth at which the derating factor is 1.0This formula gives a derating factor of 0.06 at a depth of 0.3 meters (or 1 foot). The derating factor continues to decrease with increasing depth, but it never reaches zero.

Negative Ampacity

When the derating factor is less than 1.0, it means that the ampacity of the conductor is reduced. However, it is not possible for the ampacity of a conductor to be negative. The negative ampacity in your example is a mathematical artifact of the simplified formula for the derating factor.

Difference in Ampacity Between Conductors

There is indeed a difference in ampacity between conductors at the top and bottom of a duct bank. The conductors at the bottom of the duct bank are exposed to higher temperatures due to the heat rising from the conductors above them. As a result, the ampacity of the conductors at the bottom of the duct bank is lower than the ampacity of the conductors at the top of the duct bank.The NEC does not provide a specific method for accounting for the difference in ampacity between conductors at different depths in a duct bank. However, one common practice is to use the derating factor for the depth of the lowest conductor in the duct bank. This ensures that all of the conductors in the duct bank have sufficient ampacity. Flag for review