User: ejohnson, Location: Lockport, IL
Asked on: Tuesday, January 11, 2011 at 3:58 pm EST
Answered on: Tuesday, May 14, 2024 at 12:07 am EDT
Question: NEC Article 310.60(C)(2)(b) states that ??an ampacity derating factor of 6 percent per 300-mm (1-ft) increase in depth for all values of rho shall be permitted.?. Does the derating factor not decrease with an increase in depth to a point at which it becomes zero? If not, using this derating method, there is a point at which the conductor will have negative ampacity.Example: 15kV 1/0 AWG shielded single conductor copper cable, no neutral (select smallest neutral size in table)Using table in IEEE Std. 835-1994 (pp. 349):75% load factor, 90 Rho, 90?C max. conductor temp. from table, 105?C desired conductor temp. rating, 25?C ambient temp. used in table, 21?C desired ambient temp., 0 for temp. rise due to dielectric loss, 0 for new temp. rise due to dielectric loss, 234.5 inferred temp. of zero electrical resistance, 48? burial depth to top of duct bankUsing formula from IEEE Std. 835-1994, Section 3.4.1 (pp. Intro-10): Adjusting for ambient temperature, the multiplier obtained is 1.03.Using formula from IEEE Std. 835-1994, Section 3.4.2 (pp. Intro-10): Adjusting for maximum conductor temperature, the multiplier obtained is 1.08.Derating for depth: 1.00 ? 1.5(.06) = .91Ampacity rating for 1/0 cable with 1/6 neutral: 139AI = 139*1.03*1.08*.91 = 140A (rounding down)Same example with 240? (20-ft) burial depth to top of duct bank:Derating for depth: 1-(20*12-30)/12*.06 = -.05I = 139*1.03*1.08*-.05 = -7A (rounding down)How can this be possible? Also, is there no reason to account for the difference in ampacity between conductors at the top of a duct bank and conductors at the bottom of the same duct bank?
Derating Factor
The derating factor does decrease with an increase in depth, but it does not reach zero. The formula for the derating factor is:
0.6(D - 0.3)where: D = depth in meters (or feet) 0.3 = depth at which the derating factor is 1.0This formula gives a derating factor of 0.06 at a depth of 0.3 meters (or 1 foot). The derating factor continues to decrease with increasing depth, but it never reaches zero.