Question: Hi Guys,I have a couple questions regarding the grounding of a stepdown transformer via 250.30(A)(7). The code states that the GEC for the separately derived system shall be from the water pipe or building steel. I have a case where the main panel is closer to the step-down transformer than the water pipe. Can I install the GEC for the transformer back to the ground bus at the main panel where a GEC from the water pipe and ground rod is connected? Also, if I run the GEC for the transformer to the water pipe, is a supplemental ground rod required per 250.53(D)(2). I only ask because it's not referred to in 250.30(A)(7).Thanks,Creig
Can you install the GEC for the transformer back to the main panel?
Yes, you can install the GEC for the transformer back to the ground bus at the main panel. According to 250.30(A)(7), the GEC for the separately derived system can be connected to the water pipe or building steel. Since the main panel has a GEC connected to both the water pipe and ground rod, it can serve as a suitable grounding point for the transformer.
Is a supplemental ground rod required if the GEC is connected to the water pipe?
No, a supplemental ground rod is not required if the GEC for the transformer is connected to the water pipe. 250.53(D)(2) only requires a supplemental ground rod if the GEC from the main service panel is connected to a metal underground water pipe. In this case, the GEC for the transformer is connected to the ground bus at the main panel, which is connected to both the water pipe and ground rod. Flag for review