User: Npstewart, Location: Henrico County, VA
Asked on: Wednesday, January 12, 2011 at 9:35 am EST
Answered on: Tuesday, May 14, 2024 at 12:08 am EDT
Question: After figuring the voltage drop for a particular circuit, if the conductors are required to be upsized, is the EGC ALWAYS required to be up sized?I know the EGC is based off of the rating of the OCPD and not the area as in 250.66, so how would you know which size to go with? Would it be wise to match the EGC with the new upsized feeder?Thanks!
No, the EGC is not always required to be upsized when the conductors are required to be upsized due to voltage drop. The size of the EGC is based on the rating of the overcurrent protective device (OCPD) protecting the circuit, and not on the size of the conductors.However, if the upsized conductors are required to protect against voltage drop, it is likely that the OCPD will also need to be upsized. In this case, the EGC would also need to be upsized to match the new OCPD rating.It is generally wise to match the EGC with the new upsized feeder, as this will ensure that the EGC is properly sized to protect the circuit. Flag for review