User: Michael Schneider, Location: Illinois
Asked on: Wednesday, January 12, 2011 at 9:30 am EST
Answered on: Tuesday, May 14, 2024 at 12:08 am EDT
Question: If you have a 208/120,3 phase 4 conductor circuit and the circuit is unbalanced there is current on the neutral conductor. IF you use 3 individual breakers and one neutral, and you turn one breaker off there, will be current on the neutral conductor. If you are working on the circuit you shut off, there will be current on the neutral conductor. Is this correct and how do you prevent this from happening if it is correct. Must you turn off all 3 breakers to work on any of the 3 curcuits.
Yes, the statements are correct.
When a 3-phase, 4-wire circuit is unbalanced, meaning that the currents in the three phases are not equal, there will be current flowing in the neutral conductor. This is because the neutral conductor carries the unbalanced current, which is the difference between the currents in the three phases.
If you turn off one breaker, there will still be current on the neutral conductor. This is because the neutral conductor is still connected to the other two phases, which are still carrying current.
If you are working on a circuit that is shut off, there may still be current on the neutral conductor. This is because the neutral conductor is still connected to the other two phases, which may still be carrying current.
To prevent this from happening, you must turn off all three breakers to work on any of the three circuits. This will ensure that there is no current flowing in the neutral conductor, making it safe to work on the circuit.
Alternatively, you can use a non-contact voltage tester to check the neutral conductor for voltage before working on the circuit. This will ensure that there is no voltage present on the neutral conductor, making it safe to work on the circuit. Flag for review