User: mshields, Location: Boston, MA
Asked on: Wednesday, January 12, 2011 at 2:06 pm EST
Answered on: Tuesday, May 14, 2024 at 12:09 am EDT
Question: Working on a hospital that has the following distribution:13.8kV S&C existing switchgear to remainPrimary metered.Primary switches feed each of two 2500kVA transformers which in turn feed two ends of a double ended 480V switchgear lineup.Now - We're replacing that double ended lineup as well as the two transformers lets say in kind (although now they're smaller). At present the Fire Pump is fed from a breaker in the double ended line up. I cannot immitate that I realize, but my question is do I have to tap one of the main switches in the 13.8kV gear or can I tap ahead of the 480V switchgear main. If it matters, the 13.8kV lineup and transformers are outside, the 480V switchgear is indoors.Thanks,Mike
NEC requires that Life Safety (e.g., fire pumps) be fed from the primary side of the service. Therefore, you must tap one of the main switches in the 13.8kV gear to feed the fire pump.
NEC Reference
Section 700.12(A): "Electric power from a service disconnecting means shall be supplied to the buildings or premises served by that service." Section 701.6(C): "For the purpose of this article, a service disconnecting means shall be considered one that disconnects the service conductors from the main feeder or feeders and shall not disconnect load side conductors."
Explanation:
By tapping the fire pump breaker off the main switch in the 13.8kV gear, you ensure that it is fed from the incoming service conductors and not from the load side of the transformers. This complies with NEC requirements and ensures that the fire pump will have power in the event of a failure on the secondary side of the transformers or the 480V switchgear. Flag for review