User: MBSec, Location: Iowegia
Asked on: Wednesday, January 12, 2011 at 2:12 pm EST
Answered on: Tuesday, May 14, 2024 at 12:09 am EDT
Question: I have a camera install at a new construction gas station. There are indoor cameras (no issues), cameras at the gas pumps, and cameras on light poles around the parking lot.The inspector said that the cabling needs to be 600V rated since it is inside the light pole with the 110V light circuit (the camera has its own conduit all the way to the concrete base of the lightpole). I am using cat5, and the Belden 7958a I found is $675 a box!My questions are:1. Is there an easier/less expensive way to satisfy code?2. Do I need the same cabling for the cameras mounted under the gas pump canopy (since the area is flammible)? I am running conduit down the surface of the post, with a couple feet of seal-tight up to the camera housing.3. Could any one point me to the relevant sections in the NEC?I'd really appreciate any comments/suggestions.
1. Easier/Less Expensive Way to Satisfy Code
Use a conduit liner
A non-metallic conduit liner with a 600V rating can be installed inside the existing conduit, providing protection for the cat5 cabling. This is a cost-effective solution but may require additional space in the conduit.
Consider alternative cabling
There are non-rated cat5 cables available that may be acceptable to the inspector. However, their use is not recommended in hazardous locations and may void the warranty.
2. Cabling for Gas Pump Cameras
The NEC requires 600V rated cabling for all electrical circuits within 18 inches of a flammable liquid dispensing area (NEC 514.4). Since the gas pumps are considered a flammable liquid dispensing area, you would need to use 600V rated cabling for the cameras mounted under the canopy.
3. NEC Code References
NEC 514.4: Flammable Liquids NEC 300.3(C)(1): Electrical Wiring in General NEC 700.10(B)(2): Wiring Methods in Hazardous (Classified) Locations
Additional Recommendations: Contact the local building department for clarification on code requirements. Consider hiring a licensed electrician to ensure proper installation and code compliance. Use shielded cat5 cabling to minimize electrical interference.* Ground the cable shielding to the electrical ground at both ends of the run. Flag for review