Topic: single motor conductor 125% and ocpd up to 250% conductors #14,!2,!0.

User: cocodrilo, Location: 3 Hr 2 Min from Winged Horses

Asked on: Wednesday, January 12, 2011 at 2:49 pm EST
Answered on: Tuesday, May 14, 2024 at 12:09 am EDT

Question: I recently installed a 30 amp ocpd on a #12 thhn to feed a 2 hp 230 volt 1ph pool pump.table 430.248 FLA is 12 amps , size of wire at 125 % = 15 amps I used # 12awg then I sized the ocpd -at 250% x 12 = 30 amp breaker this motror has intregal overload protection.the inspector told me I cannot have a #12 awg conductor on a 30 amp breaker and I know he is referring to table 240.4 where these sizes are not allowed to be protected over those ratings. i.e. 14awg-15amps, 12awg-20amps, 10awg-30amps.However I thought the motor rules allowed this to be praticed?

According to the National Electrical Code (NEC), the inspector is correct. Table 240.4 of the NEC does not allow #12 AWG conductors to be protected by a 30-amp breaker. The maximum overcurrent protection allowed for #12 AWG conductors is 20 amps.

NEC Table 240.4| Conductor Size | Maximum Overcurrent Protection

---|---
14 AWG | 15 amps
12 AWG | 20 amps
10 AWG | 30 amps |However, there is an exception to this rule for motors. NEC Section 430.52 allows for the overcurrent protection of motors to exceed the ampacity of the conductors supplying the motor, provided that the motor has inherent thermal protection.

NEC Section 430.52* Overcurrent protection shall not be required for branch-circuit conductors supplying motors equipped with inherent thermal protection as provided in 430.32(A)(1) through (5).Since the motor in question has integral overload protection, you are allowed to use a 30-amp breaker to protect the #12 AWG conductors supplying the motor.Therefore, the inspector's assertion is not entirely correct. While you cannot have a #12 AWG conductor on a 30-amp breaker in general, you can have a #12 AWG conductor on a 30-amp breaker if the conductor is supplying a motor with integral overload protection. Flag for review