Question: Is it o.k. to apply a higher rated voltage breaker to a lower voltage rated piece of equipment. In other words if I have a 100A 2-pole 480V breaker can I use this same breaker on a 2-pole 208V circuit?If so is the only difference the avaliable short circuit rating used at different voltages?
Yes, it is acceptable to apply a higher rated voltage breaker to a lower voltage rated piece of equipment. The higher voltage rating of the breaker indicates that it is capable of withstanding higher voltage levels without breaking down. By using a higher voltage rated breaker on a lower voltage circuit, you are ensuring that the breaker will not be damaged in the event of a voltage surge or other electrical fault.The only difference between using a higher voltage rated breaker on a lower voltage circuit is the available short circuit rating. The short circuit rating of a breaker is the maximum amount of current that the breaker can safely interrupt. The short circuit rating of a breaker is determined by the voltage rating of the breaker and the design of the breaker.For example, a 100A 2-pole 480V breaker will have a higher short circuit rating than a 100A 2-pole 208V breaker. This is because the 480V breaker is designed to withstand higher voltage levels and interrupt higher levels of current.When selecting a breaker for a particular application, it is important to consider the voltage rating of the circuit and the available short circuit current. The breaker should be rated for the voltage of the circuit and the short circuit current that is available at the point of installation. Flag for review