User: tsbichler, Location: Washington State
Asked on: Wednesday, January 12, 2011 at 7:13 pm EST
Answered on: Tuesday, May 14, 2024 at 12:10 am EDT
Question: I'm working at a VA hospital (new building). It has two services,normal and emergency, fed from different transformers. Main distribution boards are in a common electrical room. Can I upsize GEC from ufer. water pipe, and building steel for total Kcmil of both services and run it to one distribution boards' ground bar and then tap from ground bar to other distribution board? If not, do I have to run seperate GEC's to each service or use irreversible splices and tap off main upsized GEC? Prints show a ground bar on wall in electrical room. I'm guessing the engineer figured to bring common GEC's to the bar and then tap off to the two services. Would this pass code? If so, it seems less likely for a GEC to get disconnected if I do the taps at one of the distribution boards instead of out in the open like shown on prints. Also both outdoor transformers are located side by side. Should I use a common ground ring for both, or have two seperate ones?
Can I upsize GEC and run it to one distribution board's ground bar?
Yes, you can upsize the grounding electrode conductor (GEC) and run it to one distribution board's ground bar. This is permissible as long as the total cross-sectional area of the upsized GEC meets or exceeds the sum of the required areas for each service.
Do I need separate GECs or use irreversible splices?
No, you do not need separate GECs or use irreversible splices. The NEC allows for a common GEC for multiple services fed from different transformers.
Should I use a common ground ring for both transformers?
Yes, you can use a common ground ring for both transformers if they are located side by side. This will provide a more effective grounding system.
Would the ground bar solution pass code?
Yes, bringing common GECs to a ground bar and then tapping off to the two services would pass code, as long as the ground bar is sized appropriately and the taps are made securely.
Benefits of using ground bar
Reduced risk of disconnection: Concentrating the taps on the ground bar reduces the likelihood of a GEC getting disconnected out in the open. Easier maintenance: Having all the grounding connections in one location makes it easier to perform maintenance and troubleshooting.
Recommended steps:1. Calculate the required GEC size for each service using Table 250.122(C) of the NEC.
2. Upsize the GEC to meet or exceed the sum of the required areas.3. Install the upsized GEC and connect it to the ground bar on the wall.
4. Tap off from the ground bar to each distribution board's ground bus.5. Install a common ground ring around both transformers. Flag for review