Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 330.30(d)2

User: Cow, Location: Eastern Oregon

Asked on: Wednesday, January 12, 2011 at 7:43 pm EST
Answered on: Tuesday, May 14, 2024 at 12:11 am EDT

Question: Am I reading this right? I can run a 6' MC whip to a fixture with nothing more than snap-in connectors on the ends and be legal?http://www.arlcatalog.com/Flex/SNAP2IT Connectors.htmI'm so used to strapping within 12" that when I actually read the NEC article it caught me off guard....:roll:

Yes.The NEC 2014 only requires the whip to be secured within 3 feet of the fixture. Technically, if you run the whip through a conduit or cable tray from the panel, you do not need to secure the last few feet to the ceiling joists or studs. If you do not have the option to run the whip through conduit or cable tray, you will need to use some sort of support method to keep the last 3' of the whip from hanging freely. If you use snap-in connectors on the ends of the whip, you can secured the whip to the ceiling using straps, wire ties, or staples.The snap-in connector is a UL listed fitting and is considered a "connector." The "connector" is allowed to extend beyond the box or fixture. So, the snap-in connector is actually considered part of the whip and the 3' securing rule applies. Flag for review

Previous Question Next Question