Question: I have a question regarding the tap rule for 240.21(B)(1)-(5).If a UL instrument or meter is installed that is self protected and isolated such that it requires no fusing (per manufacturer's instructions) and is following the tap rule 240.21(B)(1) through (5), I have the following questions:1. The device draws two amperes maximum. What size wire is required when tapping off a 480 Volt 1000 amp service?2. Per this section of the national electric code no fusing or supplementary protection is required as long as the instrument wiring meets the section rules. Correct? In other words, the tap wiring will be less than 10 feet and goes directly to the instrument without fusing, and the instrument is mounted inside of the switchgear.Thank-you for your help.
1. Wire Size
According to 240.21(B)(1) and 240.21(B)(2), the maximum allowable ampacity of the tap conductor is 10% of the ampacity of the feeder conductors. In this case, the feeder ampacity is 1000 amps, so the maximum tap conductor ampacity is 1000 amps x 0.1 = 100 amps.Since the instrument draws a maximum of 2 amperes, any wire size that is rated for at least 100 amperes can be used. For example, a #8 AWG copper wire is rated for 120 amperes, which meets the requirement.2. Fusing or Supplementary Protection
Yes, per 240.21(B)(1) through (5), no fusing or supplementary protection is required for the tap conductor if the following conditions are met: The instrument or meter is self-protected and isolated according to the manufacturer's instructions. The tap conductor meets the requirements of 240.21(B)(1) through (5), including the distance limitations and wire size requirements.* The tap conductor is enclosed in a raceway or other suitable protection.In this case, the instrument is self-protected and isolated, the tap conductor follows the requirements of 240.21(B)(1) through (5), and the tap conductor is installed in a raceway within the switchgear. Therefore, no fusing or supplementary protection is required. Flag for review