Question: Is it a code violation (NEC or building) for conduit to be encapsulated by spray-on insulation?

Yes, it is a code violation for conduit to be encapsulated by spray-on insulation.

National Electrical Code (NEC) NEC 300.15(A)(1) states that electrical conductors shall not be installed in direct contact with thermal insulation.

International Building Code (IBC)
IBC 2603.3.6 states that electrical conductors and conduit shall not be in contact with thermal insulation.

Reasons for the Code Violation



Overheating

Spray-on insulation can restrict the flow of heat from the conduit, causing the conductors to overheat and potentially start a fire.


Moisture Penetration

Spray-on insulation can absorb moisture, which can lead to corrosion of the conduit and conductors.

Access for Maintenance

Encapsulated conduit can make it difficult to access and maintain the electrical system.

Exceptions

In some cases, spray-on insulation can be used around conduit if the following conditions are met:


The conduit is rated for use in insulated environments.
The insulation is not applied directly to the conduit. A thermal barrier is installed between the conduit and the insulation.* The electrical system is inspected and approved by the appropriate authority.

It is always best to consult with a qualified electrician or building inspector to ensure compliance with code requirements. Flag for review