Question: I have a 208:480 delta:delta transformer, corner grounded, so this question doesn't really pertain to my current installation, but in going through Art. 250 I wondered: If I had a wye secondary with unbalanced phase loads, wouldn't objectionable neutral current flow through the XF case and on the EGC from the supply? Or is the idea that the neutral current is supposed to flow on the GEC for the separately derived system (the secondary) to the Grounding electrode? This doesn't seem right either, because then you would possibly have objectionable current on exposed structural steel, for example? Any insight as to what I am missing here would be greatly appreciated.
You are correct in your understanding that an unbalanced load on a wye secondary can cause objectionable neutral current to flow through the transformer case and on the EGC from the supply. This is because the neutral current is the sum of the three phase currents, and if they are unbalanced, the neutral current will not be zero.The NEC requires that the neutral current be limited to 200% of the maximum phase current. This is to prevent the neutral conductor from overheating. In the case of a transformer with a wye secondary, the neutral current can be limited by using a zigzag grounding transformer. A zigzag grounding transformer is a special type of transformer that has a delta primary and a wye secondary. The delta primary is connected to the line side of the transformer, and the wye secondary is connected to the load side. The zigzag grounding transformer provides a path for the neutral current to flow without flowing through the transformer case or the EGC from the supply.In the case of a separately derived system, the neutral current is not supposed to flow on the GEC. The GEC is only supposed to be used to ground the system to earth. The neutral current is supposed to flow on the neutral conductor back to the transformer. If the neutral conductor is not properly sized, it can overheat and cause a fire.Exposed structural steel is not supposed to be used as a grounding electrode. This is because exposed structural steel is not a reliable grounding electrode. It can rust and corrode, which can increase its resistance and make it less effective as a grounding electrode. Flag for review