Question: I was told by an engineer and I can not get my fingers around as it seems to be circular. I have a 3-2" conduits and 3- 1 1/2" conduits entering the back of a 8 x 8 x 48" wireway. I was told I have to use the pullbox code as it is used as a pullbox not a wireway, thus using the 6 times the size of the largest conduit which would ultimately be 12" plus the additional measurement of the additional conduits which would be a wireway of 18" minimum. Is this correct and also what determines if this is used as a pullbox or wireway.
Determining Usage as Pullbox or Wireway
The NEC (National Electrical Code) defines a pullbox as a metal enclosure used to facilitate the pulling of conductors into a raceway. A wireway, on the other hand, is an enclosure used to protect wires and cables from damage.In your case, the 8 x 8 x 48" enclosure is used to enter and exit the wireway, thus serving as a pullbox.
NEC Pullbox Requirements
The NEC requires that pullboxes have a minimum dimension of 6 times the size of the largest conduit entering the box. In your case, the largest conduit is 3-2". Therefore, the minimum dimension would be 6 x 3-2" = 18".In addition, the NEC requires that for every additional conduit entering the pullbox, the minimum dimension should be increased by 6 inches. You have three additional conduits (3-1 1/2"), so the total minimum dimension would be:18" + (3 x 6") = 24"Conclusion
Based on the information provided, it is correct that you should use the pullbox code to determine the minimum dimension of the enclosure. The minimum dimension is 24". Flag for review