User: lpfam11, Location: Logan, Utah
Asked on: Thursday, January 13, 2011 at 12:33 pm EST
Answered on: Tuesday, May 14, 2024 at 12:12 am EDT
Question: NEC 110.14(C)(1) states that "Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on table 310.16....."We have sized our cables based on the 310.17 free air chart because we are in cable tray but based on above we should have used 310.16.How can I get around this and stay with the ampacities shown on table 310.17 and what is required when it says "listed and marked otherwise"?
To use the ampacities from Table 310.17 for cable tray installations, you must meet the following requirements
1. The equipment must be listed and marked for use with the higher ampacities.
This means that the manufacturer of the equipment must have specifically tested and approved the equipment for use with the higher ampacities in Table 310.17. The equipment must be marked with a label or other indication that it is approved for this use.2. The installation must meet the requirements of Table 310.
17.
This includes the following requirements: The cables must be installed in a single layer in the cable tray. The cables must be spaced at least 1 inch apart. The cable tray must be adequately ventilated to prevent the accumulation of heat. The cables must be properly supported to prevent damage.3. The installation must be inspected and approved by a qualified electrician.
The qualified electrician will verify that the installation meets all of the requirements of NEC 110.14(C)(1) and Table 310.
17.
If you are not able to meet all of these requirements, then you must use the ampacities from Table 310.16 for your cable tray installation.Additional Information:
The NEC allows the use of ampacities from Table 310.17 for cable tray installations because the free air around the cables in a cable tray provides better cooling than the still air around cables in a conduit. However, the NEC requires that the equipment be listed and marked for use with the higher ampacities to ensure that the equipment is safe to operate at these higher temperatures.If you are unsure whether your equipment is listed and marked for use with the higher ampacities in Table 310.17, you should contact the manufacturer of the equipment. Flag for review