Topic: NM entering box

User: chris kennedy, Location: Miami Fla.

Asked on: Thursday, January 13, 2011 at 2:27 pm EST
Answered on: Friday, May 24, 2024 at 3:43 pm EDT

Question: I'm having a tough time finding where the NEC states NM must enter through the fitting in the box, not in 334 so it has to be in 300. Little help please, thanks.

300.15(B)(3) Except when installed in conduit, surface raceways, or other raceways, or where otherwise specified, cables entering a box or enclosure shall enter through a knockout, a certified hub, or an approved cable connector assembly (see Figure 300.15(B)(3) and (4)). Flag for review