User: CLEMDVA, Location: Tennessee
Asked on: Thursday, January 13, 2011 at 4:49 pm EST
Answered on: Tuesday, May 14, 2024 at 12:13 am EDT
Question: My electrician is out of town till next week and my curiosity is getting the best of me. Perhaps someone can take a minute to clarify this to me, a dumb facility manager. We will be ordering a three-phase HWH next week and if I mis-identify the voltage I will be eating it.The electrical service (Virginia) is 480 4wy service per the utility (and the meter). This feeds an unlabelled cabinet which I assume houses a transformer which steps it down to three phase 208/120. From there to a sweet Square D panel (QMB type) labelled 3 phase 208/120. If I measure voltage in a three-pole disconnect I get 120 from any single pole to ground, but I don't get 208 between any two of the three, I get 212-215. I got this on all the three-pole disconnects (and with a second meter). Is this voltage within the range of tolerance?This matters as the HWH we are looking at are specific for these voltages. Don't want to spec 208 and fry the unit.Lastly, why does the meter say "4wy 120 480" -- if 480 why doesn't it say 277 somewhere? Just wonderin'.
Voltage Measurement The voltage range of 208/120 is typically considered acceptable and within industry standards. The 212-215 volts you measured is slightly higher than 208 but still within a reasonable range of tolerance. The higher voltage may be due to the fact that the transformer is not loaded to its full capacity.
Voltage Label on Meter The meter label "4wy 120 480" indicates that the electrical service is a 4-wire system with the following voltages: 120 volts from each phase to neutral 480 volts from phase to phase* The absence of "277" on the meter is because it is not a typical voltage for this type of service. 277 volts is typically used in 3-phase, 4-wire systems with a grounded neutral, which is not the case here.
Ordering the Water Heater
Based on the voltage measurements and the meter label, it is likely that you have a 3-phase, 4-wire, 208/120 electrical service. Therefore, you should specify the water heater accordingly (208-volt, 3-phase).Always consult with a qualified electrician if you have any concerns or uncertainties about electrical systems. Flag for review