Question: Hi everyone, I searched my title and couldn't find what I was looking for so I will ask.For residential street lights we set a pull box next to the utility's box, put 10amp fuses in that box then run to the pole and place 3amp fuses, there is a ground rod at the pole and our pull box, so the pole, and the two rods are bonded together, but then the ground is not bonded at the utility, there is no neutral, this a 240v system. (I hope that made enough sense to piece it together) I know that during a line to ground fault it will not open the 10a fuses, energizing the pole, I feel that this is not a safe installation, I could be wrong and hope someone could explain this to me, or tell me how the rest of the world ties in their flat rate street light poles. (flat rate being that their is no service).Thank you

The installation you describe does not meet the requirements of the National Electrical Code (NEC) and poses a safety hazard.

NEC Requirements for Street Lighting Section 410.30(C) requires that street lighting fixtures be grounded. Section 410.30(D) requires that the grounding electrode system for street lighting fixtures be connected to the neutral conductor, if available, and if not, to a grounding electrode. Section 250.50 requires that all equipment be bonded to the grounding electrode system.

Safety Hazard

In your installation, the grounding is not bonded at the utility box, creating an open circuit. This means that during a line-to-ground fault, the fault current will not be able to flow to ground, and the pole will become energized. This poses a serious safety hazard to anyone who touches the pole.

Proper Installation

To ensure a safe installation, you should:1. Connect the grounding conductor from the pole to the neutral conductor in the utility box. If there is no neutral conductor, connect the grounding conductor to a grounding electrode, such as a ground rod driven into the earth.
2. Bond all equipment, including the pole, the pull box, and the ground rods, together with a properly sized bonding conductor.

Alternative Approaches

In some cases, it may not be possible to connect the grounding conductor to the neutral or a grounding electrode at the utility box. In such cases, the following alternative approaches can be considered:
Isolated Neutral System

In this system, the neutral conductor is isolated from ground at the utility transformer. This requires special equipment and precautions, and should only be done by qualified personnel.

Ground-Fault Circuit Interrupters (GFCIs)

GFCIs can be installed on the street light circuit to detect ground faults and interrupt the circuit.


Wireless Street Lights

Wireless street lights do not require a physical connection to the power grid, eliminating the need for grounding.

Conclusion


It is essential to ensure that street lighting installations are safe and compliant with the NEC. The installation you described poses a safety hazard and should be corrected immediately. Flag for review