Question: Is it permitted by the NEC to tap a 125 amp feeder with 3 # 10 and run it 60' before hitting OCP? What code articles is this?
According to the National Electrical Code (NEC), it is not permitted to tap a 125 amp feeder with 3 #10 conductors and run it 60 feet before hitting an overcurrent protective device (OCP).
NEC Articles Referenced
Article 240.13(A): Conductors entering a panelboard shall be protected by an overcurrent device rated not greater than the allowable ampacity of the conductor. Article 310.16: For conductors rated 10 AWG or smaller, the allowable ampacity shall be determined by Table 310.16 based on the type of conductor, insulation, and installation method.
Explanation:
The allowable ampacity of three #10 AWG conductors in parallel is approximately 40 amps, according to Table 310.16. Therefore, these conductors cannot safely handle the current required by a 125 amp feeder.By running the feeder 60 feet without an OCP, there is a risk of overloading the conductors and causing a fire hazard. An OCP is required to protect the conductors by interrupting the circuit if the current exceeds their allowable ampacity.To comply with the NEC, either: The feeder must be protected by an OCP rated for 125 amps or less. The feeder must be run using conductors rated for at least 125 amps. Flag for review