Question: In case you have't guessed, I've been doing some breaker research lately.I noticed that as breaker voltage ratings increase the interrupting capacity of the breaker decreases. Why is this? Is this becasue for a given system there will be less avaliable fault current at higher voltages?Also does anyone know why the breaker interrupting ratings change when applied to frequencies other than 60hz?Lastly I saw a statement stating that the voltage rating is determined by the maximum voltage that can be applied across its terminals. Is this referring to L-G for each of the terminals?
Relationship between Voltage Rating and Interrupting Capacity
Yes, you are correct. As breaker voltage ratings increase, the interrupting capacity of the breaker typically decreases. This is because: Higher Voltage = Lower Impedances
At higher voltages, the impedance of the circuit decreases, resulting in increased fault currents.
Constant Interrupting Time
Circuit breakers have a specific interrupting time that remains constant regardless of voltage.
Energy Let-Through
The energy let-through by the breaker is proportional to the square of the fault current and the interrupting time.Therefore, with higher fault currents at higher voltages, the breaker must limit the energy let-through by reducing its interrupting time, which leads to a lower interrupting capacity.
Breaker Interrupting Ratings at Different Frequencies
Breaker interrupting ratings can change at frequencies other than 60 Hz due to several factors: Arc Extinction
The frequency of the current affects the arc extinction process. Higher frequencies can make it more difficult to extinguish the arc.
Capacitive Effects
High-frequency currents can cause capacitive coupling effects that can affect the breaker's ability to interrupt the fault.As a result, breakers may have different interrupting ratings at different frequencies.
Voltage Rating and Maximum Terminal Voltage
The voltage rating of a breaker is indeed determined by the maximum voltage that can be applied across its terminals, typically specified as line-to-ground (L-G) voltage. This means that: The breaker can withstand the maximum L-G voltage without experiencing breakdown or insulation failure.* It can interrupt fault currents up to its interrupting capacity at the maximum L-G voltage.Understanding the relationship between voltage rating and interrupting capacity, as well as the impact of frequency on breaker performance, is essential for selecting and applying circuit breakers appropriately. Flag for review