Topic: Transformer secondary protection

User: rifi, Location: Logan, Utah

Asked on: Friday, January 14, 2011 at 3:35 pm EST
Answered on: Tuesday, May 14, 2024 at 12:15 am EDT

Question: We were recently asked to install a 75 KVA, 480v primary/ 120/208v secondary transformer to match other similar installations already installed at this R&D center. The primary was protected with a 90 amp, 480 volt breaker, and the secondary conductors which were 3/0 THHN, went to a 200 amp main breaker on a panel. However, previous to feeding this 200 amp breaker, a tap was made to another 200 amp main breaker and panel. All secondary wiring is 3/0, and the distances from the transformer to the first panel is 40' and an additional 25' to the second. Is this secondary protection Code compliant?

No, the secondary protection is not Code compliant.

NEC Requirements



NEC 450.3(A)(1)
requires that overcurrent protection for transformer secondary conductors be rated not more than the secondary conductor ampacity. NEC 450.3(A)(2) requires that the protection for the secondary conductors be placed at the point where the conductors originate.

Analysis

The 3/0 THHN conductors have an ampacity of 230 amps. The 200 amp main breakers on the panels are not rated sufficiently to protect the 3/0 conductors. The tap made before the first panel is a violation of NEC 450.3(A)(2), as it does not provide protection at the point where the conductors originate.

Corrective Action:


To make the installation Code compliant, the following corrective actions are required:
Replace the 200 amp main breakers on the panels with 230 amp main breakers. Remove the tap before the first panel and install a new 230 amp main breaker at the point where the conductors originate. Ensure that all branch circuit breakers and conductors downstream of the panels are properly sized for the load. Flag for review