Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Question on size of service conductors for multifamily bldg.

User: aksparky, Location: Logan, Utah

Asked on: Friday, January 14, 2011 at 3:42 pm EST
Answered on: Tuesday, May 14, 2024 at 12:16 am EDT

Question: I have a 5 unit bldg I need to hang a service on, the 5 unit service pack I am getting carries a 400 amp rating.When I did the load calculation for all 5 units it computes to approx. 215 amps (all gas appliances and laundry is house panel).Questions is, doesnt the load calculation dictate the size of the wire pulled up the mast for the service point not the rating of the gear?Thanks in advance for any input

Yes, the load calculation should dictate the size of the wire pulled up the mast for the service point.

The load calculation determines the total amperage demand of all the electrical devices in the building. This determines the minimum ampacity (current-carrying capacity) of the service conductors required to safely supply electricity to the building.

The service pack rating

The rating of the service pack (in this case, 400 amps) is the maximum current it can safely handle. It does not necessarily reflect the actual load demand of the building. The service pack must be rated for at least the calculated load of the building, but it can be higher.

Code Requirements

Electrical codes typically require that the service conductors be sized based on the calculated load, not the service pack rating. This ensures that the conductors can safely carry the actual electrical demand of the building.

In your case

The calculated load is approximately 215 amps. You should pull up wires with an ampacity of at least 215 amps to the service point. The 400-amp service pack may provide additional capacity for future expansion or oversized equipment.

Conclusion:


The load calculation should always dictate the size of the service conductors. The service pack rating is important for ensuring the safety and reliability of the electrical system, but it does not override the load calculation requirements. Flag for review

Previous Question Next Question