Topic: Cable Tray

User: Enile, Location: Nevada

Asked on: Friday, January 14, 2011 at 4:46 pm EST
Answered on: Tuesday, May 14, 2024 at 12:16 am EDT

Question: Hi all, I have two questions regarding cable trays.I can size the cable tray with one of the four cases that NEC describes, but I think theres one case missing, and that is mixing cables from 1/0 up to 1000kcm.For example, say I have 6-3/0 cables and 6-300kcm cables. I can assume that, by using the "equation":A ? (1.1 Sd)And making "Sd=0" (because theres no 1000kcm or bigger cables), I can use case 2.Is that rigth? or how do you size the cable tray?Also, NEC also states that if you bundle conductors they can be "installed in other than a single layer", so, if you dont want the ampacity increase by spacing them 2.15 times the OD, Can you place the bundled conductors without spacing and use 310.17 ampacities multiplied by 0.65?

Question 1: Sizing Cable Tray for Mixed Cable Sizes

Yes, your assumption is correct. For mixed cable sizes, you can use the formula:

A ≥ (1.1 Sd)
where: A = required cross-sectional area of cable tray Sd = sum of conductor cross-sectional areas in kcmilsSince there are no cables larger than 1000kcm in your example, you can assume Sd = 0 and use Case 2 of the NEC cable tray sizing rules.

Question 2: Ampacity of Bundled Conductors

No, you cannot place bundled conductors without spacing and use the ampacities from Table 310.17 multiplied by 0.
65.If you do not want to increase the ampacity by spacing the bundled conductors 2.15 times the OD, you must use the ampacities from Table 310.15, which are already based on bundled conductors without spacing. Flag for review