Topic: Multiple motors, largest is intermittent though

User: Finite10, Location: Great NW

Asked on: Friday, January 14, 2011 at 6:56 pm EST
Answered on: Tuesday, May 14, 2024 at 12:16 am EDT

Question: Several motors -fused with an inverse time delay breaker. The largest motor was also 5 minute intermittent duty cycle.Not sure if I should take the largest motor at 125% as in 430.24 and ignored the 110% short-time duty percentage in Table 430.22(E), or what?

According to the National Electrical Code (NEC)

For

continuous duty motors
, use the motor nameplate current to determine the ampacity of the circuit conductor and protective device. For intermittent duty motors, you must multiply the motor nameplate current by the applicable percentage from Table 430.22(E) to determine the circuit conductor and protective device ampacity.

In your case

The largest motor is

5-minute intermittent duty cycle
. Table 430.22(E) states that for intermittent duty cycle motors, you must use 110% of the motor nameplate current.

Therefore, you should take the largest motor at 110% (not 125%) of its nameplate current.Steps to Calculate Circuit Ampacity

1. Determine the nameplate current of the largest motor.
2. Multiply the motor nameplate current by 110%.3. The result is the minimum ampacity required for the circuit conductor and protective device.


Example

If the nameplate current of the largest motor is 10 amps, then the minimum circuit ampacity required is:10 amps x 110% = 11 amps

Note:


The inverse time delay breaker should be selected to have a trip curve that coordinates with the overload characteristics of the motors. The time delay will allow the motors to start and operate without tripping the breaker during normal operation, but will trip in the event of an overload or short circuit. Flag for review