Topic: air handler name plates

User: sparky333, Location: Eighty Four,Pa.15330

Asked on: Saturday, January 15, 2011 at 5:56 am EST
Answered on: Tuesday, May 14, 2024 at 12:17 am EDT

Question: I have been an electrician for over 20 years and a journeyman for 16 .But I have been confused over the name plates on these new units i have been wiring. this is just an example.208/240 volts then the ampacitys will say 35/40 for whatever heat strips are in that unit.This is just an example with the ampacitys >my question is How Come the smaller Number is on the left Of the slash?.My knowledge has always been that at 208 Volts the amps will be larger then at 240v and vice versa. the more volts the less amps.Right ?Just like a name plate on a motor is right 120/240v then the amps is like 20/10a just an exampleor a three phase 208/480 = more/less ampscould some on please help me out with this?

The smaller number on the left of the slash (/) on the nameplate of an electrical unit indicates the ampacity of the unit when operating at the higher voltage (240 volts in your example), while the larger number on the right indicates the ampacity when operating at the lower voltage (208 volts).This naming convention is used because the ampacity of a conductor decreases as the voltage increases. This is because the power (watts) consumed by a device is the product of the voltage and the current, and for a given power level, the higher the voltage, the lower the current must be.For example, if an electrical unit has a nameplate rating of 208/240 volts, 35/40 amps, it means that the unit can operate at either 208 volts or 240 volts, but the maximum current it can draw at 240 volts is 35 amps, while the maximum current it can draw at 208 volts is 40 amps.This is important to consider when sizing wiring and circuit breakers for electrical installations. The wiring and circuit breakers must be rated for the maximum current that the unit can draw at the voltage it will be operating at.In the case of your example, if the unit is operating at 240 volts, the maximum current it can draw is 35 amps, so the wiring and circuit breaker must be rated for at least 35 amps. However, if the unit is operating at 208 volts, the maximum current it can draw is 40 amps, so the wiring and circuit breaker must be rated for at least 40 amps. Flag for review

Previous Question Next Question