Question: I have an issue with an inspector i would like help solving. I have an a/c that has 23.2 min ckt ampacity with max breaker size of 30. What size wire can i run and what is the code article. I ran 12 ga. per art 440.6(a) and table 310.16. 12 ga thhn is good for 30 amps. For motor loads and compressors do the * apply on table 310.16?
Applicable Code Article and Wire Size
NEC Article 430.22 (A) requires the ampacity of the branch-circuit conductors to be at least 125% of the motor full-load current (FLC). NEC Table 430.248 provides FLC values for various motor types. NEC Article 440.6(A) allows for the use of Table 310.16 to determine the ampacity of conductors for air-conditioning and refrigeration equipment.
In this case
The motor FLC is not provided. We can use the maximum breaker size (30 amps) as an estimate of the motor FLC (assuming no overload protection). Table 430.248 does not provide an FLC for an air-conditioning compressor, so we cannot use it to calculate the required ampacity.
Therefore, we can use the following equation to estimate the required ampacityRequired Ampacity = 125% x Maximum Breaker Size = 125% x 30 amps = 37.5 amps
Table 310.16 shows that
12 AWG THHN wire has an ampacity of 25 amps 10 AWG THHN wire has an ampacity of 30 amps
Conclusion
Since the required ampacity is 37.5 amps,
10 AWG THHN wire is the minimum wire size that can be used, as it has an ampacity of 30 amps.
Note: The on Table 310.16 applies to motor loads and compressors. In this case, the load is an air-conditioning compressor, which is considered a motor load. Therefore, the applies. Flag for review