Topic: Mike Holt Master/Contractor Simulated Exam, part 3, question 15, pg 18 -2008 NEC

User: Finite10, Location: Great NW

Asked on: Sunday, January 16, 2011 at 6:17 pm EST
Answered on: Tuesday, May 14, 2024 at 12:19 am EDT

Question: This question is regarding the Calculations section of Mike's book;What is the code reference that tells me to use the nameplate rating FLA, and not the NEC Table 430.248 FLC?The answer key says to use the nameplate FLA, not FLC.I've dug around and can't find it. Confused, please help.

The reference for using the nameplate FLA is found in the 2020 NEC 430.248(A). It states: "The rating of a motor in horsepower shall be considered the nameplate rating and shall be the basis for calculating branch-circuit requirements." Flag for review