Topic: grounding electrode conductor VS.Equipment grounding conductor

User: [email protected], Location: Plant city,fl

Asked on: Sunday, January 16, 2011 at 9:14 pm EST
Answered on: Tuesday, May 14, 2024 at 12:19 am EDT

Question: 1.Is a grounding electrode a ground rod,pipe,building steel or plate?2.Is the grounding electrode conductor the wire that connects to the grounding electrode's?3.Is 250-66 the table in the nec that this wire GEC size is found?4.Does the grounding electrode conductor terminate in the meter can?Now, does the same size wire as the GEC run out of the metercan to the disconnect and on to the panel? OR Do you go to 250-122 and change the wire size becuase it now becomes the Equipment grounding conductor? Realizing that 250-66 size's don't match 250-122 size's. Can someone explane please?Thank You,Stafford Electric

  1. Yes, a grounding electrode can be a ground rod, pipe, building steel, or plate.2. Yes, the grounding electrode conductor is the wire that connects to the grounding electrode.
    3. Yes, 250-66 is the table in the NEC that specifies the size of the grounding electrode conductor.4. No, the grounding electrode conductor does not terminate in the meter can. It terminates at the grounding electrode.The wire that runs from the grounding electrode, through the meter can, to the disconnect and on to the panel is the equipment grounding conductor (EGC). The size of the EGC is determined by 250-122. The size of the GEC is determined by 250-66. The sizes of the GEC and EGC do not necessarily match.In general, the EGC will be smaller than the GEC. This is because the EGC only carries fault currents, while the GEC carries both fault currents and lightning currents.
Flag for review

Previous Question Next Question