User: wmeek, Location: Texas
Asked on: Monday, January 17, 2011 at 10:21 am EST
Answered on: Tuesday, May 14, 2024 at 12:20 am EDT
Question: I was wanting to make sure I was figuring this right. I have a 3 phase 320 Meter can with a 3" rigid riser with 3-500mcm and 1-350 mcm conductors. My total load calculation is 320A. By code i can go down to these 500 mcm conductors as long as toal load does not exceed 380A. Is this a correct install. Also has anyone installed parallel 2" for the primary side of meter can. I know meter can comes with a single hole for a hub, but was wanting to see if anyone has installed a myers hub for second conduit. Would this be legal per code.Thanks
1. Cable Sizing for Conduit
Yes, the cable sizing is correct. According to Table 310.15(B)(16) of the NEC, the ampacity of a 500 MCM copper conductor in a 3-inch rigid riser is 380A. Therefore, since the total load is 320A, the use of 500 MCM conductors is permitted.
2. Parallel 2-Inch Conduits for Primary Side
While it is not specifically prohibited by the NEC, installing parallel 2-inch conduits for the primary side of a meter can is not common practice. The meter can is typically designed with a single hub for the primary conduit.
3. Myers Hub for Second Conduit
Using a Myers hub to add a second conduit to the meter can is likely not legal per code. The NEC requires that conductors be installed in an approved raceway. While a Myers hub is a type of conduit fitting, it is not designed as a raceway and does not provide the same level of protection as an approved conduit.
Recommendation:
If you need to run additional conductors to the meter can, it is recommended to use a separate conduit and hub. This will ensure that the installation is compliant with code requirements and provides proper protection for the conductors. Flag for review