Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: bonding at the service

User: zombie, Location: pennsylvania

Asked on: Monday, January 17, 2011 at 3:07 pm EST
Answered on: Tuesday, May 14, 2024 at 12:20 am EDT

Question: Where service conductors are installed in parallel, the total circular mil area of the conductors connected in parallel for one phase are added together to determine the main bonding jumper. Ex. Three 250 kcmil in parallel would be treated as a 750 and would get a 2/0 main bonding jumper.My question is does this same rule apply for an equipment bonding jumper on the supply side of the service

Yes. The same rule applies for an equipment bonding jumper on the supply side of the service. The total circular mil area of the parallel conductors is added together when sizing the equipment bonding jumper. Flag for review

Previous Question Next Question