Topic: Auto transformer help

User: bluemoon7799, Location: Ann Arbor, Michigan

Asked on: Monday, January 17, 2011 at 4:22 pm EST
Answered on: Tuesday, May 14, 2024 at 12:21 am EDT

Question: Hey all,I am in need of some help. We have a project where I need to step down a 3 phase 230V, 60hz wye supply (although there is no 4 th wire [secondary voltage used]) to 115V 3 phase supply. But the catch is that because of space restraints in the cabinet the PM wants to use auto transformers (UGHH) to acheive this because of the space savings. From what I have been reading you cannot have a 3 phase delta (or wye) to delta auto transformer. Is there a configuration that can be used to acheive the desired voltage supply with auto transformers?Thanks

Using Autotransformers for 3-Phase Voltage Conversion

While it is not possible to directly use autotransformers for 3-phase delta to delta conversion, there are alternative configurations that can achieve the desired voltage supply

1. Single-Phase Autotransformers in Bank (Open Delta)
Connect two single-phase autotransformers in an "open delta" arrangement. Phase A autotransformer: Connect S1 to line A and S2 to line B. Phase B autotransformer: Connect S1 to line B and S2 to line C. Phase C: Leave open (phase C voltage is obtained by bridging lines A and B).2. Dual-Voltage Autotransformers with Isolation Transformer Use three dual-voltage autotransformers with an optional isolation transformer. Autotransformers: Connect S1 to line A, S2 to line B, and S3 to line C. Isolation transformer: Connect the primary to the 230V supply and the secondary to the load. This configuration provides isolation between the input and output.3. Buck-Boost Transformer with Isolation Transformer Use a three-phase buck-boost transformer with an optional isolation transformer. Buck-boost transformer: Connect the primary to the 230V supply. Isolation transformer: Connect the secondary of the buck-boost transformer to the primary of the isolation transformer. Connect the secondary of the isolation transformer to the load. This configuration provides isolation and voltage regulation.

Considerations
Autotransformers have issues with current balancing, and any load imbalance can cause overheating. The configurations described above introduce potential safety hazards due to the open connection in the open delta method and the increased leakage inductance in the other methods. Proper safety measures, such as current balancing relays and grounding, must be implemented.

Recommendation

Due to the limitations and potential safety concerns, it is recommended to consider using a step-down transformer instead of autotransformers for this application. Step-down transformers are more reliable and provide better voltage regulation. Flag for review