Question: I am installing a fused motor disconnect for a 10hp, 208 volt 3 phase motor.The nameplate says it is 30.8 FLA with a locked rotor current of 179 amps.430.103 commentary in the 2008 handbook says the disconnect shall be capable of interrupting the locked rotor current of the motor which I believe the fuses will take care of.430.110 says that I need to size the disconnect at 115% of the FLA,430.110.C (1) Says the rating of the disconnecting means shall be determined from sum of all currents at the full load condition and also at the locked rotor condition. But this is for Combination Loads which I dont believe applies to single motors.Question #1- If I size the disconnect at 115% of the FLA andf make sure it is rated for the 10HP wouldnt that comply with code? (Which would be a 60amp disconnect using Time Delay Fuses rated at 15HP).Question #2- Under what circumstance would we have to use the Locked Rotor Condition to size a disconnect?If I had to use ther LRA at 179 amps my disconnect would have to be a 200 amp disconnect for a 30.8 amp load which seems crazy, I would like to know because next time it might be a disconnect for a combination load.Thanks in advance for any input

Question #1

Yes, sizing the disconnect at 115% of the FLA would comply with the code, assuming it is also rated for the 10HP motor. For a 208V, 3-phase motor, the FLA is 30.8 amps, so a 60-amp disconnect with Time Delay Fuses rated at 15HP would meet this requirement.

Question #2

You would have to use the Locked Rotor Condition (LRA) to size a disconnect in the following circumstances:

Combination Loads

As per 430.110.C(1), the rating of the disconnecting means for combination loads must be determined from the sum of all currents at the full load and locked rotor conditions.


Frequent Starting or Stopping

If the motor is expected to start and stop frequently, the LRA may be a significant factor in sizing the disconnect. This is because the disconnect must be able to withstand the high currents that occur during locked rotor starting.However, for a single motor load, such as the 10HP, 208V, 3-phase motor in your case, it is generally not necessary to use the LRA to size the disconnect. The FLA is a more practical and sufficient measure for this purpose.

Additional Notes:
When selecting Time Delay Fuses, ensure they have a suitable time-current characteristic to protect the motor from both short-circuit and overload conditions. The disconnect switch should be rated for the full load current of the motor and should have an interrupting rating equal to or greater than the locked rotor current of the motor. Flag for review