Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ring Terminals

User: john8791, Location: Iowa, US

Asked on: Monday, January 17, 2011 at 5:19 pm EST
Answered on: Tuesday, May 14, 2024 at 12:21 am EDT

Question: Working in a manufacturing plant on a 480V (Wye) supplied cabinet that has a PLC controller for a nickel plating line along with a various control relays, etc. On the outside of the cabinet is mounted a 480V-120V transformer (2 wire secondary) that supplies control circuits as well as a boiler circulation motor.The secondary of this transformer is not grounded (which is what I am going to do). I noticed rather than using a ground bus bar, the person who wired it took all the grounds to a 1/2" stud on the galvanized base plate in the cabinet. There are about 5 ground wires ranging 14 to 10ga crimped into ring terminals and put on the one stud. Is there any restriction that limits how many ring terminals on one stud? I have not found anything in the NEC handbook. I am inclined to put in two bus bars; one for the grounds, and one for the "neutral" of the transformer and then bond the two together. Any thoughts? Thanks

NEC Requirements

The National Electrical Code (NEC) does not explicitly limit the number of ring terminals that can be connected to a single ground stud. However, it does require that all grounds be connected to a common ground point (Article 250.4(A)(5)).

Best Practices

While the NEC does not have specific limitations, industry best practices recommend limiting the number of ring terminals on a single stud to a reasonable number. This helps to ensure reliable grounding and prevent overheating or damage to the stud.

Grounding Bus Bars vs. Stud

Using a ground bus bar instead of a stud is generally considered a better practice for several reasons: Increased Surface Area

Bus bars provide more surface area for the grounding connections, improving conductivity and reducing resistance.


Organization

Bus bars allow for a more organized and efficient grounding system, making it easier to identify and connect grounds.

Versatility

Bus bars can accommodate a wider range of wire sizes and types, including stranded and solid conductors.

Bonding Ground and Neutral


The neutral conductor of the transformer should be bonded to the equipment grounding conductor at the transformer. This bonding is required by NEC Article 250.30(A)(1) to establish a reference potential and ensure proper operation of equipment.

Recommendation

Based on best practices, it is recommended to:
Install two bus bars, one for grounds and one for the transformer's neutral. Bond the two bus bars together. Connect the ground wires to the ground bus bar and the neutral wire to the neutral bus bar.* Use ring terminals designed for the appropriate wire size and torque them properly.By following these recommendations, you will ensure a safe and reliable grounding system for your equipment. Flag for review