Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Chimney top draft inducer motor

User: Ken 6789, Location: Raeford, NC

Asked on: Tuesday, January 18, 2011 at 1:20 am EST
Answered on: Tuesday, May 14, 2024 at 12:22 am EDT

Question: I plan on wiring in a stainless steel draft inducer on a chimney top. The motor housing is approx 18" tall and approx 18" diameter. The chimney is approx 20' above grade. The motor is 120 volt and draws less than an amp. I am wondering if it is necessary (I believe yes) to bond a GEC to the unit housing and down to a ground rod and also bond it to the electrical service GEC on the opposite side of the house. The instructions does not mention anything about bonding the housing to a GEC and only an EGC is needed to ground the housing. My concern is the possibility of a lighting strike to the unit and traveling through the EGC. I never installed anything like this and just seeking a second opinion. Thanks.

Yes, it is necessary to bond the stainless steel draft inducer housing to a Grounding Electrode Conductor (GEC).Reasons



Lightning Protection

A lightning strike to the unit could travel through the EGC to the electrical service GEC. By bonding the unit housing to a separate GEC, you create a low-resistance path for lightning current to flow directly to ground, reducing the risk of damage to the unit or the structure.


Safety

In the event of an electrical fault or short circuit, the bonding connection ensures that current flows through the proper grounding path, protecting against electrical shock and fire hazards.

Code Compliance

The National Electrical Code (NEC) requires that all metallic enclosures of electrical equipment be grounded.

Bonding Procedure

Install a GEC in accordance with local codes. A minimum of a 3/4-inch copper rod or 6-foot ground rod is recommended. Connect a #8 AWG solid copper wire to the GEC. Attach the other end of the wire to a grounding lug on the unit housing. Run a separate #8 AWG copper wire from the unit housing to the electrical service GEC.

Additional Notes:
The EGC is still necessary to ground the motor and prevent it from becoming energized. The instructions may not mention grounding the housing because it is typically assumed that the unit will be installed on a metal chimney that is already grounded. It is good practice to refer to the NEC for specific grounding requirements in your area. Flag for review

Previous Question Next Question