Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Egc

User: sbutler, Location: North Charleston, SC

Asked on: Tuesday, January 18, 2011 at 10:19 am EST
Answered on: Tuesday, May 14, 2024 at 12:22 am EDT

Question: I have a 4.16kv chiller that has RGSC from switchgear to 3' above connection box. Then it transistions to LFMC (< 6') to the connection box. Is an EGC required to be run with the feeder cables or can the conduit be the EGC? Per 250.118, (6)e, it appears as though it is required.Thanks for any and all replies.

Yes, an EGC is required to be run with the feeder cables.

According to NEC 250.118(6)(e), for feeders supplying equipment where the supply circuit continues through the equipment to supply other equipment, an EGC shall be provided with the feeder conductors to the equipment. This is to ensure a continuous EGC path throughout the electrical system.In this case, the feeder cables for the chiller supply power from the switchgear to the connection box. The connection box then distributes power to other equipment. Therefore, an EGC must be provided with the feeder cables to the connection box.The fact that the conduit is LFMC (< 6') does not change this requirement. LFMC can only be used as an EGC if it meets the requirements of NEC 250.118(10), which are more stringent than the requirements for feeder cables. In this case, LFMC is not a suitable EGC because it is not bonded to the equipment at both ends of the run. Flag for review

Previous Question Next Question