Topic: Nec 314.27 (a)(1)

User: erickench, Location: Brooklyn, NY

Asked on: Tuesday, January 18, 2011 at 10:22 am EST
Answered on: Tuesday, May 14, 2024 at 12:22 am EDT

Question: Hi guys, I'm preparing a new proposal for the above NEC section. There seem's to be a problem with the language. The present 2011 NEC state's the following:Boxes used at luminaires or lampholder outlets in a wall shall be marked on the interior of the box to indicate the maximum weight of the luminaire that is permitted to be supported by the box in the wall, if other than 23 kg (50 lb).The problem is the word "other" used in this NEC section. "Other" implies that the permitted weight of the box could be less than or greater than 50 lbs. What I need to know is what is the present practice of the manufacturers? Do they mark the box if it can hold more than 50 lbs or less? I'm an engineer not an electrician. I nor the CMP expects the manufacturers to change their practices on account of any proposal that I make.

Industry Practice

According to industry sources, manufacturers typically mark luminaire support boxes with the following: If the box is rated for more than 50 lbs, it will be marked with the maximum weight it can support (e.g., "100 lbs max"). If the box is rated for 50 lbs or less, it will not have any specific weight marking.Therefore, the current practice is that manufacturers mark boxes that can hold more than 50 lbs, but not those that can hold 50 lbs or less.

Interpretation of NEC Section

The use of the word "other" in NEC 314.29 implies that there are two possibilities:1. The box is rated for more than 50 lbs (indicated by a specific weight marking).
2. The box is rated for less than 50 lbs (not indicated by any weight marking).This interpretation is consistent with industry practice, which uses weight markings to indicate capacities greater than 50 lbs.

Proposal Considerations

When preparing your proposal, you may want to consider: Clarifying the language

Remove the word "other" and replace it with "greater than" to explicitly state that boxes are marked if they support more than 50 lbs.


Aligning with industry practice

Ensure that the proposed language aligns with the current practices of manufacturers to avoid confusion.*

Impact on existing installations:
Consider the potential impact on existing installations that may have luminaire support boxes marked for less than 50 lbs. Flag for review