Topic: Expansion fittings

User: Ohmboy, Location: Logan, Utah

Asked on: Tuesday, January 18, 2011 at 10:32 am EST
Answered on: Tuesday, May 14, 2024 at 12:23 am EDT

Question: Are expansion fittings required where RMC emerges from underground and terminate in an enclosure located on the outside of a building.I can locate the code ref. for pvc but cant find it for RMC. Thanks

Yes, expansion fittings are required where RMC emerges from underground and terminates in an enclosure located on the outside of a building.

Code Reference

* [NEC 358.28(B)(1)](https://www.nfpa.org/NEC/NEC-Articles/Article-358)

Explanation:


RMC (rigid metal conduit) is a type of electrical conduit that is made of galvanized steel. It is used to protect electrical wires and cables from physical damage, moisture, and other environmental hazards.Expansion fittings are required for RMC conduit that emerges from underground because the conduit can expand and contract due to changes in temperature. This expansion and contraction can put stress on the conduit and its connections, which can lead to damage.Expansion fittings provide a flexible connection between the conduit and the enclosure. They allow the conduit to move without putting stress on the connection. This helps to prevent damage to the conduit, the enclosure, and the electrical wires and cables inside. Flag for review