Topic: romex in conduit

User: romex jockey101, Location: Silicon Valley, California

Asked on: Tuesday, January 18, 2011 at 11:26 am EST
Answered on: Tuesday, May 14, 2024 at 12:23 am EDT

Question: ive ran a few circuits in the past to garages and instead of running single conductors i just pulled romex through the pvc i couldnt find in the code if this is allowed i see it alot as well...one guy told me you should take the outer shething off when you put nm in conduit... from now on ill pull stranded conductors through just wanted to no the code on it.....also can you put mc in emt ?

NM Cable in Conduit Allowed

Yes, with specific conditions.


NEC Reference

Article 334.15(B)

Conditions for NM Cable in Conduit

Conduit must be smooth-walled (e.g., EMT, PVC) with a diameter not less than 6 times the outside diameter of the cable (see NEC Table 350.15(B)(3)). Outer sheath of the NM cable

must not
be removed. Cable must be securely fastened to the box or fitting at each end. Conduit must be installed in accordance with Article 334 (Securely fastened, no sharp bends, etc.).

MC Cable in EMT Allowed

Yes


NEC Reference

Article 324.7(B)(1)

Conditions for MC Cable in EMT

EMT must be threaded or securely fastened at all couplings and boxes. MC cable must be secured to the EMT at intervals not exceeding 3 feet. The MC cable must be securely terminated at each end.

Additional Notes:
Using stranded conductors in conduit is generally preferred due to better flexibility and ease of pulling. Threaded EMT provides a more secure connection than compression fittings. Always follow the NEC and applicable local electrical codes when performing electrical work. Flag for review