Topic: Nec 695.5(c)(2)

User: erickench, Location: Brooklyn, NY

Asked on: Tuesday, January 18, 2011 at 11:59 am EST
Answered on: Tuesday, May 14, 2024 at 12:23 am EDT

Question: The above NEC section refers to transformers being connected to feeders in multi-building complexes. I'm trying to interpret this section and see exactly how the OCPD is to be sized for the transformer feeders. My interpretation is that the primary feeder OCPD is selected according to NEC 450.3 while the secondary feeder OCPD is selected to carry the locked rotor currents of the fire pump motor plus the pressure maintenance pump motor plus the F.L.C. of the associated fire pump accessory equipment plus 100% of the remaining loads. Is this correct?

Yes, that is a correct interpretation of the NEC section referenced. Here is a breakdown of the OCPD sizing requirements

Primary Feeder OCPD:
Selected according to NEC 450.3, which specifies the OCPD size for transformer primary conductors. Typically, this means sizing the OCPD to carry the full-load current of the transformer plus any additional loads connected to the primary side.

Secondary Feeder OCPD

Sized to carry the following loads: Locked rotor current of the fire pump motor Locked rotor current of the pressure maintenance pump motor Full-load current (FLC) of the associated fire pump accessory equipment 100% of the remaining loads connected to the secondary side of the transformer

100% of Remaining Loads

This refers to all other non-fire pump loads connected to the secondary side of the transformer, such as lighting, receptacles, and HVAC equipment.

Note:
The OCPD for the secondary feeder must be sized to handle the combined load of the fire pump loads and the remaining loads. This ensures that the transformer can safely supply power to all connected loads, including during fire pump operation. Flag for review