User: jtashaffer, Location: KY
Asked on: Tuesday, January 18, 2011 at 12:10 pm EST
Answered on: Tuesday, May 14, 2024 at 12:23 am EDT
Question: What are the codes for running conduit in wet locations?
National Electrical Code (NEC)Section 352.10 Conduit Bodies and Fittings 352.10(A) General. Conduit bodies and fittings installed in wet locations shall be of the raintight type. 352.10(B) Two-Piece Conduit Bodies. Two-piece threaded conduit bodies shall be used with a gasket. 352.10(C) Single-Piece Conduit Bodies. Single-piece threaded conduit bodies shall be installed with a compound or sealing washer. 352.10(D) Nonmetallic Conduit Bodies and Fittings. Nonmetallic conduit bodies and fittings shall be listed for use in wet locations.
Section 358.4 Outdoor Installations of Conductors. 358.4(B) Drip Loops. Service conductors and other conductors shall have drip loops made on them where they enter a building. The drip loops shall be formed to prevent water from entering the building along the conductors. 358.4(C) Outdoor Location. Conductors shall be installed outdoors as follows
Be installed in a raceway or cable tray that is approved for outdoor use. Be supported by a messenger or other means approved for outdoor use. Be coated with a moisture-resistant finish.
Section 404.9 Junction Boxes, Device Boxes, and Conduit Bodies for Use in Wet Locations. 404.9(A) General. Junction boxes, device boxes, and conduit bodies installed in wet locations shall be listed for use in wet locations.* 404.9(B) Covers. Covers shall be closed and secured to prevent water from entering the box. Flag for review