User: wmeek, Location: Texas

Asked on: Tuesday, January 18, 2011 at 1:11 pm EST
Answered on: Tuesday, May 14, 2024 at 12:23 am EDT

Question: If the utility requires a ground in the meter can to the neutral bar, isn't that the same as bonding the neutral. If so, would that be per code to bond the neutrals again in service disconnect.

Yes, grounding the neutral bar in the meter can is the same as bonding the neutral.The neutral is bonded to ground at the service entrance. This is typically done in the main breaker panel or in the meter can. Bonding the neutral at the service entrance ensures that the neutral is at the same potential as the ground. This is important for safety because it prevents electrical shocks.Bonding the neutral again in the service disconnect is not necessary. However, it is not a code violation to do so.It is important to note that the neutral should only be bonded to ground at one location. Bonding the neutral at multiple locations can create a ground loop, which can cause electrical problems. Flag for review