User: fosilfuel, Location: Eastern Mojave Desert
Asked on: Tuesday, January 18, 2011 at 1:28 pm EST
Answered on: Tuesday, May 14, 2024 at 12:24 am EDT
Question: We have a newly installed Schedule 40 PVC Conduit running underneath a concrete slab. If we pull a 4/0 THWN Type TC cable rated at 90C through the PVC, will we have to derate the cable temp rating to 75C?Also what's the best way to protect the PVC? It's rising out of the concrete on one side and dirt on the other.Thanks and any help would be appreciated.
Temperature Rating
No, you do not have to derate the cable temperature rating to 75°C. Schedule 40 PVC conduit has a maximum allowable temperature rating of 90°C, which is the same as the temperature rating of the 4/0 THWN Type TC cable. Therefore, the cable can be operated at its full rated temperature without derating.
Protection of PVC Conduit
To protect the PVC conduit from damage, you can use the following methods: Rising Out of Concrete
Seal the top of the conduit with a weatherproof sealant to prevent moisture penetration. Install a flexible conduit extension above the concrete surface to accommodate expansion and contraction. Secure the conduit to the concrete with conduit straps or pipe hangers.
Rising Out of Dirt
Install a length of concrete-filled conduit or pipe sleeve around the PVC conduit to protect it from physical damage. Seal the top of the conduit with a weatherproof sealant. Backfill around the conduit with clean, compacted soil. Consider installing a concrete pad or slab around the base of the conduit for additional protection.
Additional Considerations: Ensure that the PVC conduit is properly sized for the cable being installed. Lubricate the cable before pulling it through the conduit to reduce friction and prevent damage. Use a pulling compound or tape to protect the cable from abrasion. Provide sufficient bending radius for the cable to prevent damage. Install the conduit in accordance with the manufacturer's instructions and applicable electrical codes. Flag for review