Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Mechanical Gas pipe on a cable tray support

User: onelilvictory, Location: Indiana

Asked on: Tuesday, January 18, 2011 at 1:59 pm EST
Answered on: Tuesday, May 14, 2024 at 12:24 am EDT

Question: Can anyone tell me if it is a violation of the NEC to have a mechanical gas pipe installed off of a cable tray support? If so, (which I believe it is a violation) can anyone direct me to the code reference?Thanks!Rod

Yes, it is a violation of the NEC to have a mechanical gas pipe installed off of a cable tray support.Code Reference



NFPA 70 - National Electrical Code (NEC)
Section 392.3(B)(2): "Cable trays shall not be used to support equipment other than electrical equipment."* Section 392.9(C)(3): "Cable trays shall not be used to support auxiliary equipment, such as mechanical piping, conduit, or ventilation systems." Flag for review

Previous Question Next Question