Question: Would the output amperage of a 45KVA xfmr wired at 480V primary be 216A with a 208/120 secondary?
No, the output amperage of a 45kVA transformer wired at 480V primary would not be 216A with a 208/120V secondary.
Correct Calculation
Using the formula Power (VA) = Voltage (V) * Current (A), we can calculate the output amperage as follows:Output amperage = Power (VA) / Voltage (V)Output amperage = 45,000 VA / 208 V (assuming 208V is the voltage on the secondary side)Output amperage =
216.34 A
Therefore, the output amperage of the transformer would be approximately 216.34A, not 216A. Flag for review