Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sizing an 400A Service

User: wmeek, Location: Texas

Asked on: Tuesday, January 18, 2011 at 5:39 pm EST
Answered on: Tuesday, May 14, 2024 at 12:24 am EDT

Question: I am installing a 400A 120/240V 3 phase service. I will be using a 320 Meter can with a 3" riser with 3-500mcm,1-350mcm. On the load side I will be double lugging and running two sets of #3/0 into two 2" conduits , one 2" to a 200A 3phase fusible disconnect, 1-2" conduit to a 200A single phase disconnect. The PoCo requires us to run a #6 conductor from the meter can to a ground rod. I also will have a Water pipe GEC conductor of #1/0 per 250.66, Bldg. steel GEC of #1/0 per 250.66. I was planning to run water pipe,and Bldg. steel GEC conductors to a junction box and set a Ground bar, and from there run a #4 Thhn to each service disconnects. Is there anything that I might have missed here in order to be code compliant. I appreciate any feed back that you give. I have never done A 400A service before.

Meter Can and Conductors

The 320 Meter can size with a 3" riser is appropriate for the 500mcm and 350mcm conductors. Confirm that the meter can is rated for the 400A service.

Load Side Distribution

Double lugging is acceptable. Ensure the #3/0 conductors are rated for 200A and are properly sized for the length of the conduit run. The 200A 3-phase fusible disconnect and the 200A single-phase disconnect are adequately sized for the 400A service.

Grounding

The #6 conductor from the meter can to the ground rod is required by the PoCo and is Code-compliant. The #1/0 water pipe and building steel GEC conductors are sized appropriately per 250.66. A junction box with a ground bar is an acceptable method for connecting the GEC conductors. The #4 THHN conductor from the ground bar to the service disconnects is acceptable for grounding the equipment.

Additional Considerations

Verify that the service entrance equipment is rated for 400A. Obtain necessary permits and inspections. Ensure that all connections are tight and secure. Install conduit straps or hangers as required for proper support. Label all conductors and equipment clearly.

Code References:
NEC 230.95: Service Entrance Conductors NEC 230.97: Meter Socket Enclosures NEC 250.66: Grounding Electrode Conductor NEC 250.104: Equipment Grounding Flag for review

Previous Question Next Question