Topic: Photo cell & Timeclock

User: Sheetrockman, Location: Chapel Hill, NC

Asked on: Tuesday, January 18, 2011 at 7:31 pm EST
Answered on: Tuesday, May 14, 2024 at 12:25 am EDT

Question: My client wants certain lights to come on at dusk, turn off during the night, turn back on before they open and then go off at dawn. I have done this before but the electrician we have now says it can't happen with one photo cell and time clock. Is this possible to do on one set up and if so i just need a quick run down on the wiring? I have my idea but would like to get another opinion.

Yes, it is possible to control lights to come on at dusk, turn off during the night, turn back on before opening, and then go off at dawn with one photocell and time clock.Wiring Setup

1.

Connect the photocell to the time clock

- Connect the photocell's "Common" terminal to the time clock's "Photocell" terminal.- Connect the photocell's "Light" terminal to the time clock's "Light" terminal.2.

Connect the time clock to the circuit breaker

- Connect the time clock's "Load" terminal to the circuit breaker that controls the lights.3.

Connect the lights to the circuit breaker

- Connect the lights' wires to the circuit breaker's terminals.

Time Clock Settings



Dusk On Time

Set the time clock to turn the lights on at your desired dusk time.


Night Off Time

Set the time clock to turn the lights off during the night (e.g., midnight).

Morning On Time

Set the time clock to turn the lights on again before the store opens (e.g., 5 AM).


Dawn Off Time

Set the time clock to turn the lights off at your desired dawn time.

How It Works

The photocell detects the ambient light level. At dusk, when the light level drops below the photocell's threshold, it sends a signal to the time clock. The time clock turns on the lights at the pre-programmed Dusk On Time. At the Night Off Time, the time clock turns off the lights. Before the store opens, the time clock turns the lights back on at the Morning On Time. At dawn, when the light level increases above the photocell's threshold, the time clock turns off the lights at the pre-programmed Dawn Off Time.

Notes:
Use a time clock with a photocell override feature to ensure the lights turn on at dusk and off at dawn, regardless of the time clock's settings. The photocell should be installed in a location where it receives unobstructed daylight.* You may need to adjust the time settings slightly after installation to fine-tune the operation. Flag for review